Lurker News
Back to discussion

Comment by vel0city

vel0city1 reply#
The poster was speaking more of the power delivery going to the power supplies, not the server's power supplies themselves. So say each PSU 1 is wired to circuit A, each PSU 2 is wired to circuit B. Circuit A experiences a failure. All servers instantly switch over all their load to their PSU 2's on circuit B. Suddenly circuit B's load is roughly double what it was just moments ago. If proper planning wasn't created or followed, this might overload circuit B, meaning all PSU 2's go dark regardless of the server being able to do the change over or not.
dijit#
Yeah I understand on re-reading: but that's also not how people run datacenters.

Obviously people can operate things however they want, but you wont get a tier 3 classification with that setup.